Transformer Oil Diagnostics

Transformer Oil Diagnostics

In addition to dissipating heat due to losses in a transformer, insulating oil provides a medium with high dielectric strength in which the coils and core are submerged. This allows the transformers to be more compact, which reduces costs. Insulating oil in good condition will withstand far more voltage across connections inside the transformer tank than will air. An arc would jump across the same spacing of internal energized components at a much lower voltage if the tank had only air. In addition, oil conducts heat away from energized components much better than air.

Over time, oil degrades from normal operations, due to heat and contaminants. Oil cannot retain high dielectric strength when exposed to air or moisture. Dielectric strength declines with absorption of moisture and oxygen. These contaminants also deteriorate the paper insulation. For this reason, efforts are made to prevent insulating oil from contacting air, especially on larger power transformers. Using a tightly sealed transformer tank is impractical, due to pressure variations resulting from thermal expansion and contraction of insulating oil. Common systems of sealing oil-filled transformers are the conservator with a flexible diaphragm or bladder or a positivepressure inert-gas (nitrogen) system. Reclamation GSU transformers are generally purchased with conservators, while smaller station service transformers have a pressurized nitrogen blanket on top of oil. Some station service transformers are dry-type, self-cooled or forcedair cooled.

Conservator System

A conservator is connected by piping to the main transformer tank that is completely filled with oil. The conservator also is filled with oil and contains an expandable bladder or diaphragm between the oil and air to prevent air from contacting the oil. Figure 1 is a schematic representation of a conservator system (figure 1 is an actual photo of a conservator).

Figure 1: Conservator with Bladder

Figure 1: Conservator with Bladder

 

Air enters and exits the space above the bladder/diaphragm as the oil level in the main tank goes up and down with temperature. Air typically enters and exits through a desiccant-type air dryer that must have the desiccant replaced periodically. The main parts of the system are the expansion tank, bladder or diaphragm, breather, vent valves, liquid-level gauge and alarm switch. Vent valves are used to vent air from the system when filling the unit with oil. A liquid-level gauge indicates the need for adding or removing transformer oil to maintain the proper oil level and permit flexing of the diaphragm.

Oil-Filled, Inert-Gas System

A positive seal of the transformer oil may be provided by an inert-gas system. Here, the tank is slightly pressurized by an inert gas such as nitrogen. The main tank gas space above the oil is provided with a pressure gauge (figure 12. Since the entire system is designed to exclude air, it must operate with a positive pressure in the gas space above the oil; otherwise, air will be admitted in the event of a leak. Smaller station service units do not have nitrogen tanks attached to automatically add gas, and it is common practice to add nitrogen yearly each fall as the tank starts to draw partial vacuum, due to cooler weather. The excess gas is expelled each summer as loads and temperatures increase. Some systems are designed to add nitrogen automatically (figure 2) from pressurized tanks when the pressure drops below a set level. A positive pressure of approximately 0.5 to 5 pounds per square inch (psi) is maintained in the gas space above the oil to prevent ingress of air. This system includes a nitrogen gas cylinder; three-stage, pressure-reducing valve; high-and low-pressure gauges; high-and low-pressure alarm switch; an oil/condensate sump drain valve; an automatic pressure-relief valve; and necessary piping.
 

Figure 2: Typical Transformer Nitrogen System

Figure 2: Typical Transformer Nitrogen System

 

The function of the three-stage, automatic pressure-reducing valves is to reduce the pressure of the nitrogen cylinder to supply the space above the oil at a maintained pressure of 0.5 to 5 psi. The high-pressure gauge normally has a range of 0 to 4,000 psi and indicates nitrogen cylinder pressure. The low-pressure gauge normally has a range of about -5 to +10 psi and indicates nitrogen pressure above the transformer oil. In some systems, the gauge is equipped with high- and low-pressure alarm switches to alarm when gas pressure reaches an abnormal value; the high-pressure gauge may be equipped with a pressure switch to sound an alarm when the supply cylinder pressure is running low. A sump and drain valve provide a means for collecting and removing condensate and oil from the gas. A pressure-relief valve opens and closes to release the gas from the transformer and, thus, limit the pressure in the transformer to a safe maximum value.

As temperature of a transformer rises, oil expands, and internal pressure increases, which may have to be relieved. When temperature drops, pressure drops, and nitrogen may have to be added, depending on the extent of the temperature change and pressure limits of the system.

.

Related articles

 

번호 제목 등록인 등록일 추천수 조회수 비고
385 [기사실기] CLF(고압한류형퓨즈) (0) 김대호 교수 2017-03-01 176 2308
384 [기사실기] PF(전력용 파워퓨즈) (0) 김대호 교수 2017-03-01 149 1661
383 [기사실기] Air Circuit Breaker(기중차단기) (0) 김대호 교수 2017-03-01 206 2758
382 [기사실기] Auto Transfer Switches(비상전원절체개폐기) (0) 김대호 교수 2017-03-01 162 1788
381 [기사실기] Interrupter Switches(인터럽터 스위치) (0) 김대호 교수 2017-03-01 141 1559
380 [기사실기] 수배전반 (0) 김대호 교수 2017-03-01 158 2034
379 [기사실기] AC vs. DC (0) 김대호 교수 2017-02-28 136 1784
378 [기사실기] How Electric Motors are made (0) 김대호 교수 2017-02-28 123 1739
377 [기사실기] Induction Motor (0) 김대호 교수 2017-02-28 154 1646
376 [기사실기] How does an Induction Motor work ? (0) 김대호 교수 2017-02-28 169 1626
375 [기사실기] Brushless DC Motor, How it works ? (0) 김대호 교수 2017-02-28 178 1598
374 [기사실기] 직류전동기의 원리 영상 Work of DC motor (0) 김대호 교수 2017-02-28 156 1726
373 [기사실기] 3상 변압기의 구조 Construction of three phase transformer (0) 김대호 교수 2017-02-28 175 2191
372 [기사필기] 변압기 원리 (2) working of transformer (0) 김대호 교수 2017-02-28 177 2006
371 [기사필기] 변압기 원리 (1) What is power transfomer ? (1) 김대호 교수 2017-02-28 179 1879
370 [기사필기] 코일피치 (0) 김대호 교수 2017-02-28 156 2225
369 [기사필기] 전자 Electron (0) 김대호 교수 2017-02-28 180 2391
368 [기사실기] 브흐홀쯔 계전기 (0) 김대호 교수 2017-02-27 187 2979
367 [기사실기] Transformer Oil Diagnostics (콘서베이터) (0) 김대호 교수 2017-02-27 184 2765
366 [기사실기] 변압기 외형 (0) 김대호 교수 2017-02-27 153 1797
추천
목록
회사소개 이용약관 개인정보취급방침 이메일주소무단 수집거부 광고문의 도서배송 관리자쪽지 찾아오시는길
사이트 이용문의 : 0505-233-3314 FAX : 02-6442-6402 이메일주소 : pekor@naver.com 대표 : 강명아
주소 : 서울특별시 서초구 효령로 41, 1층 통신판매등록번호 : 2010-서울서초-0491
사업자등록번호 : 114-90-85522 스카이미디어(교육청 평생교육시설) 개인정보관리책임자 : 강명아

Since2004, Copyright ⓒ 2024 스카이미디어 / 전기스쿨 All Rights Reserved. Ver 3.4